I have a digital Honeywell wall thermostat, and having issues.
This particular one is located on the first floor, as I have a 2 zone system. I have the thermostat set at 65 degrees, but the temperate display is showing 77 degrees. The appl I have on my mobile also indicates 77 I've tried resetting, and shutting thermostat on/off but no change. I recently replaced the battery with a fresh one. Upstairs zone is set at 55 degrees, and noticiebly much cooler upstairs so assuming that is working OK. That thermostat is old Honeywell dial-type. Thoughts on what is happening here before I run to Lowes for a new thermostat. Could the issue be at the furnace side for that zone, and ignoring the thermostat setting ? Thanks for your feedback ! |
![]() |
![]() |
![]() |
#2 |
Senior Member
Join Date: Jan 2012
Posts: 2,091
Thanks: 64
Thanked 744 Times in 478 Posts
|
![]()
Call Honeywell.
They have likely seen this before. Does it feel like 77 is correct? |
![]() |
![]() |
![]() |
#3 |
Senior Member
Join Date: Jan 2010
Posts: 191
Thanks: 695
Thanked 56 Times in 40 Posts
|
![]()
I would say flow check on boiler on that zone is stuck open allowing heat to gravity feed
|
![]() |
![]() |
![]() |
#4 |
Senior Member
Join Date: Apr 2004
Posts: 2,591
Thanks: 150
Thanked 229 Times in 166 Posts
|
![]()
Do you have forced hot water? If so the zone valve controlling that particular zone may be stuck open constantly sending hot water through the area...
|
![]() |
![]() |
![]() |
#5 |
Senior Member
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,570
Thanks: 3,204
Thanked 1,101 Times in 793 Posts
|
![]()
Problems with zone valve are common. Check the zone valve. Also check to see it the thermostat is clean of dust and that the thermostat is set to the right voltage in the line. There is a dial under the cover.
__________________
Someday may never be an actual day. |
![]() |
![]() |
Sponsored Links |
|
![]() |
#6 |
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,445
Thanks: 339
Thanked 118 Times in 95 Posts
|
![]()
Dpg & Broadhoper,
I believe you nailed it 'Zone Valve' ! Called oil dealer service and described the problem, and they said 'Zone Valve' ! It appears to be only 1 zone in question. I have Taco Zone valve, and supposedly they can be replaced easily, screw off, screw on ! Service tech on his way. Thanks to you both ! Will report back after Tech reviews. |
![]() |
![]() |
![]() |
#7 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,080
Thanks: 2,199
Thanked 1,185 Times in 752 Posts
|
![]()
I had this problem many years ago. I had 3 zones and the main one would not shut down. I didn't have zone valves, I had separate circulators and check valves. I finally confirmed it was the check valve that was stuck open. I took apart the one that was sticking and found a piece of black rubber stuck holding the check valve open. Problem fixed, or so I thought.
A week later it did it again. I took the valve apart and found another piece of black rubber. Not knowing a whole lot about plumbing and heating I tolded my burner guy about what I found and he told me the expansion tank was coming apart inside. I changed the expansion tank and problem was solve for good. |
![]() |
![]() |
![]() |
#8 |
Senior Member
Join Date: Apr 2004
Posts: 2,591
Thanks: 150
Thanked 229 Times in 166 Posts
|
![]()
bigdog - you lucked out pretty quick response this time of the year. Most of those folks right now are running like crazy.
|
![]() |
![]() |
![]() |
#9 |
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,445
Thanks: 339
Thanked 118 Times in 95 Posts
|
![]()
Have to give a shout out to my oil dealer 'Dutile Oil'.
Have been with them for 10 yrs now and they are rock solid on service ! Mike the owner is a great guy, and en expert trouble-shooter, and had this one figured out in about 10 min ! ![]() |
![]() |
![]() |
![]() |
#10 | |
Senior Member
Join Date: Apr 2004
Posts: 2,591
Thanks: 150
Thanked 229 Times in 166 Posts
|
![]() Quote:
![]() ![]() |
|
![]() |
![]() |
![]() |