Old 08-23-2014, 07:20 PM   #1
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default Code requirement for deck posts

It's been a while since I've built a deck and was wondering if the post that the beam sits on has to be 6" x 6". The last time I built one it was Ok to use 4" x 4" posts. This deck will be built in Tuftonboro.

The reason I ask is because on page 7 of the Prescriptive Residential Wood Deck Construction Guide which is based on the 2009 International Residential Code states this: "POST REQUIREMENTS....
All deck post sizes shall be 6x6 (nominal) or larger"


I don't want to make a drawing for the permit using 4" posts and find out that I need 6" posts.


Here is the Guide: http://www.awc.org/publications/dca/dca6/dca6-09.pdf
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-23-2014, 08:22 PM   #2
jeffatsquam
Senior Member
 
Join Date: Oct 2009
Location: moultonborough/sandwich
Posts: 187
Thanks: 173
Thanked 77 Times in 50 Posts
Default

Regardless of the code a 4x4 will support the load but a 6x6 will give you many more joining options which is very importune in decks.

A lot of lateral loads there.

The cost of a 6x6 over a 4x4 is minimal as is code
jeffatsquam is offline   Reply With Quote
The Following User Says Thank You to jeffatsquam For This Useful Post:
Rusty (08-27-2014)
Old 08-23-2014, 08:46 PM   #3
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

You're right about the options and price. However I was just wondering if the code requires a 6".

A friend of mine in Wolfeboro built a deck and he said the Code Enforcement Officer required a 6" post with the deck only @ 4 ft off the ground.

I guess I could ask the CEO of Tuftonboro but I would like to know where the requirement comes from if in-fact I have to.
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-26-2014, 04:06 PM   #4
TheProfessor
Senior Member
 
Join Date: Nov 2010
Posts: 1,142
Thanks: 17
Thanked 349 Times in 211 Posts
Default

Codes were brought up in another post.
I am not an expert on such.
My understanding is that there are national codes, state codes, and even local codes.

Over a decade ago or longer.
This is how I recall the story.
Spec. House.
Builder constructed a home to sell. Did all the correct permits.
This was about the time that the roof shingle companies manufactured a roof shingle that stated on instructions - that tar/felt paper is not required.
So the roof was put on per manufacturers information.
Except the local building inspector stated in "our" town we require felt/tar paper under all shingles. New roof had to be removed and redone.

Could be an urban myth story. But this was told to me by another builder.
TheProfessor is offline   Reply With Quote
The Following User Says Thank You to TheProfessor For This Useful Post:
Rusty (08-27-2014)
Old 08-27-2014, 08:07 AM   #5
Great Northern Cleaning
Senior Member
 
Join Date: Mar 2010
Location: Belmont
Posts: 89
Thanks: 17
Thanked 37 Times in 26 Posts
Default Just had this beauty....

Built at our camp. And they used 6 x 6 posts!
Attached Images
 
Great Northern Cleaning is offline   Reply With Quote
The Following User Says Thank You to Great Northern Cleaning For This Useful Post:
Rusty (08-27-2014)
Sponsored Links
Old 08-27-2014, 08:33 AM   #6
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by Great Northern Cleaning View Post
Built at our camp. And they used 6 x 6 posts!
That is a very well designed and built deck.
What size are the Band and Rim joist?

I also like the teak color of your camp.
Attached Images
 
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-27-2014, 11:01 AM   #7
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

It may be the view in the photo but what the heck is holding up the right corner of that landing?It looks like just a gusset from the main stair post.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 08-27-2014, 02:32 PM   #8
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by SIKSUKR View Post
It may be the view in the photo but what the heck is holding up the right corner of that landing?It looks like just a gusset from the main stair post.
I would say the "HUGE" ledger board is holding up that part of the deck.

That's why I asked what size Band and rim joists were used. They look really big.
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-27-2014, 02:48 PM   #9
Great Northern Cleaning
Senior Member
 
Join Date: Mar 2010
Location: Belmont
Posts: 89
Thanks: 17
Thanked 37 Times in 26 Posts
Default Rim and Band Joists....

I have been waiting for a reply back from my friend who built the deck..
But no response yet. I believe they are 2 x 10s. I can tell ya this is one
rugged deck...and there is no play or bounce on the top corner of the stairs.
Great Northern Cleaning is offline   Reply With Quote
The Following User Says Thank You to Great Northern Cleaning For This Useful Post:
Rusty (08-27-2014)
Old 08-27-2014, 04:24 PM   #10
LIforrelaxin
Senior Member
 
LIforrelaxin's Avatar
 
Join Date: May 2006
Location: Texas, Lake Ray Hubbard and NH, Long Island Winnipesaukee
Posts: 2,889
Thanks: 1,040
Thanked 896 Times in 528 Posts
Default

The only way to know for sure, what the two CEO is going to require is to speak directly to them. By the way this is what they are there for, it is their job, to not only make sure the rules are followed, but to also make available the information need, to properly plan a project.

Over the years requirements have changed tremendously regarding decks. I remember being told that are deck was built almost to rugged, and that we over engineered it. By today's standards it is not beefy enough.

The bottom line is post specification, my have lots of variables, such has how many posts are being used, over what span. etc. In the deck shown by GNC I have no doubt that 6x6 post where required. That is a fairly decent span for only 3 Posts. And then you look at the bulk of the landing being suported by a single post. Looking at the span if only 4X4 where used I would have suggested at least 4 and maybe 5 posts.

In the end you are likely to be better off just going with the 6x6 posts, they will provide stability, and for a small cost difference take the question out of the equation.

It is likely the 4x4 and 6x6 are both allowed, what you have to show is the engineering wise the structure can support an X lbs. load per square foot of surface area. The question is do you want to do the engineering work to show that your design with 4x4 will support the needed load, or just use 6x6 instead, and not have the question raised.
__________________
Life is about how much time you can spend relaxing... I do it on an island that isn't really an island.....
LIforrelaxin is offline   Reply With Quote
Old 08-27-2014, 05:50 PM   #11
Great Northern Cleaning
Senior Member
 
Join Date: Mar 2010
Location: Belmont
Posts: 89
Thanks: 17
Thanked 37 Times in 26 Posts
Default I stand corrected...

Those are 2 x 12s
Great Northern Cleaning is offline   Reply With Quote
Old 08-27-2014, 06:13 PM   #12
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

That's what I thought.

Thank you and I really like the deck!
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-27-2014, 06:56 PM   #13
DickR
Senior Member
 
Join Date: Apr 2008
Location: Moultonborough
Posts: 757
Thanks: 4
Thanked 259 Times in 171 Posts
Default

In most cases, a 4x4 post has plenty of load-bearing capacity for what it has to carry. More typically, it is a matter of height/diameter limitation. Even when a 4x4 is adequate from the engineering point of view, a 6x6 is so much stiffer that the extra cost is peanuts vs the extra robustness of the structure.
DickR is offline   Reply With Quote
Old 08-28-2014, 07:40 AM   #14
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Just rec'd the answer to my question from the CEO of Tuftonboro:

"I will allow 4x4 post under a deck no longer than six feet in length."

Now I can finalize my drawings to use 6" post.

I would have submitted a drawing with 4" post because that is how I have always built them. Also the deck is only 4ft high.
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 08-28-2014, 12:06 PM   #15
BroadHopper
Senior Member
 
BroadHopper's Avatar
 
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,600
Thanks: 3,237
Thanked 1,113 Times in 799 Posts
Default Website for building codes.

http://www.nahb.org/reference_list.aspx?sectionID=224

I always refer to the current residential building codes. However as stated in another thread towns are always behind adopting the latest RBC.
__________________
Someday may never be an actual day.
BroadHopper is offline   Reply With Quote
The Following User Says Thank You to BroadHopper For This Useful Post:
Rusty (08-28-2014)
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -4. The time now is 03:04 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.

This page was generated in 0.10441 seconds