Quote:
Originally Posted by Slickcraft View Post
Our hyper heat units 100% crossover efficiency is at about 0 deg F and they are good for operation down to minus 13 deg and 85% efficiency. However, when the temp drops below 0 deg I shut them off and switch to oil heat for zones not covered by the pellet stove. So I would not run them this Friday night.

Alan
I have never had mini splits in the same home as oil, so unable to do a direct comparison, but I am confused by your math or maybe by terminology. If mini splits are, say, 30% (or more) more efficient than oil, and they are operating at 85% efficiency at -13, aren't they still more efficient than oil at that temp? Thanks
FlyingScot is offline   Reply With Quote
Old 02-02-2023, 09:09 PM   #2
Slickcraft
Senior Member
 
Join Date: Mar 2008
Location: Welch Island and The Taylor Community
Posts: 3,388
Thanks: 1,260
Thanked 2,148 Times in 983 Posts
Default

Quote:
Originally Posted by FlyingScot View Post
I have never had mini splits in the same home as oil, so unable to do a direct comparison, but I am confused by your math or maybe by terminology. If mini splits are, say, 30% (or more) more efficient than oil, and they are operating at 85% efficiency at -13, aren't they still more efficient than oil at that temp? Thanks

The math is straightforward. At minus 15 deg 85% efficient means 100 watts in gets only 85 watts of heat out. Over 0 deg temp the efficiency is over 100% so the heat pump puts out more watts than what is required to run the unit.

The above has nothing to do with comparison with oil heat. That said, the advantage over oil is temp dependent and numbers like 30% are on average. At 10 below zero best to run the oil burner.

Alan
Slickcraft is offline   Reply With Quote
Old 02-03-2023, 10:44 AM   #3
FlyingScot
Senior Member
 
Join Date: Jun 2016
Location: Tuftonboro and Sudbury, MA
Posts: 2,552
Thanks: 1,413
Thanked 1,075 Times in 668 Posts
Default

Quote:
Originally Posted by Slickcraft View Post
The math is straightforward. At minus 15 deg 85% efficient means 100 watts in gets only 85 watts of heat out. Over 0 deg temp the efficiency is over 100% so the heat pump puts out more watts than what is required to run the unit.

The above has nothing to do with comparison with oil heat. That said, the advantage over oil is temp dependent and numbers like 30% are on average. At 10 below zero best to run the oil burner.

Alan
Yes, this is why I am confused. I understand that a minisplit on warmer days is better than a minisplit on colder days. But the question is whether a minisplit on colder days is better than oil on colder days. If a minisplit is 30% better than oil in general, and oil is assumed to be always at 100% of its own efficiency, then doesn't the minisplit need to fall to 70% efficiency before oil is equal, and 69% before oil is more efficient? If all of this is the case, then the minisplit on a -13 day at 85% is still the best choice
FlyingScot is offline   Reply With Quote
Old 02-03-2023, 10:53 AM   #4
ishoot308
Senior Member
 
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 6,538
Thanks: 2,455
Thanked 5,468 Times in 2,143 Posts
Default

Quote:
Originally Posted by FlyingScot View Post
Yes, this is why I am confused. I understand that a minisplit on warmer days is better than a minisplit on colder days. But the question is whether a minisplit on colder days is better than oil on colder days. If a minisplit is 30% better than oil in general, and oil is assumed to be always at 100% of its own efficiency, then doesn't the minisplit need to fall to 70% efficiency before oil is equal, and 69% before oil is more efficient? If all of this is the case, then the minisplit on a -13 day at 85% is still the best choice
Isn't the efficiency of an oil burner on average around 85%?? I realize some of the newer ones are better but for the most part 85% is pretty standard is it not?? Which would mean the mini split at -5 would be far more efficient would it not??

Dan
__________________
It's Always Sunny On Welch Island!!
ishoot308 is offline   Reply With Quote
Old 02-03-2023, 12:45 PM   #5
John Mercier
Senior Member
 
Join Date: Jun 2021
Posts: 4,009
Thanks: 3
Thanked 680 Times in 562 Posts
Default

Quote:
Originally Posted by ishoot308 View Post
Isn't the efficiency of an oil burner on average around 85%?? I realize some of the newer ones are better but for the most part 85% is pretty standard is it not?? Which would mean the mini split at -5 would be far more efficient would it not??

Dan
If it put out enough BTUs at the lower efficiency.
John Mercier is offline   Reply With Quote
Sponsored Links
Old 02-03-2023, 01:22 PM   #6
DickR
Senior Member
 
Join Date: Apr 2008
Location: Moultonborough
Posts: 765
Thanks: 4
Thanked 260 Times in 172 Posts
Default

Quote:
Originally Posted by Slickcraft View Post
The math is straightforward. At minus 15 deg 85% efficient means 100 watts in gets only 85 watts of heat out. Over 0 deg temp the efficiency is over 100% so the heat pump puts out more watts than what is required to run the unit....
I think the term "efficiency" is being misused here (for a minisplit). The performance of a heat pump in heating mode generally is indicated by "Coefficient of Performance" (COP), that being the ratio of energy delivered inside (as heat) to energy input as electrical power (3412 BTU/hr per KW). A reasonable seasonal averaged COP might be around 3, but this will be substantially higher when the outside temerature is say in the 40s or 50s. The COP also drops as outside temperature drops. Think of it as being like pumping water uphill; for a given amount of pump power, you get a lower flow as you pump farther uphill.

That 85% number for the minisplit likely indicates how much of full rated capacity (BTU/hr) is being delivered from a very cold outside temperature. In general, except for some losses along the path, a heat pump delivers as heat all of the electrical energy input to the compressor plus whatever is absorbed from the source (outside air) by the evaporation of refrigerant on the cold (low pressure) side. Thus the COP will always be above 1.0 and substantially so.

It should be noted that heat pumps installed in heating climates generally are sized according to the expected heating load at some design minimum heat loss rate, which can be calculated sufficiently well for any house. On the other hand, most fired heat systems installed over the years typically are grossly oversized relative to expected demand, often by a factor of 2 to 4. Such a system has a lot of extra capacity, which leads to short cycling in normal use but which does let a cold house recover rapidly after a power outage or other period of deep setback. In contrast, a properly sized heat pump does not have that huge reserve of overcapacity for rapid recovery.
DickR is offline   Reply With Quote
The Following User Says Thank You to DickR For This Useful Post:
ishoot308 (02-03-2023)
Old 02-03-2023, 08:10 PM   #7
Biggd
Senior Member
 
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,433
Thanks: 2,432
Thanked 1,271 Times in 814 Posts
Default

My wood stove has been blasting out heat for two straight days now and I'm just able to keep the house at 68 degrees tonight, and it's a well insulated home. I have oil heat and I don't think that would keep up at these temperatures. I doubt a Mini Split would keep up tonight, it's -12 right now in Meredith.
Biggd is offline   Reply With Quote
Old 02-02-2023, 09:20 PM   #8
Descant
Senior Member
 
Join Date: Mar 2006
Location: Merrimack and Welch Island
Posts: 4,600
Thanks: 1,418
Thanked 1,705 Times in 1,109 Posts
Default

With no direct experience, just quotes from vendors, I have the impression that as temperature drops, so does efficiency of the mini-splits. However, that says to me that they don't fail to heat, it just costs more to run them. If the temp drops to 0 F I pay more for oil and the electricity to pump the hot water or hot air around the house. Presumably, I pay more for the mini splits to operate as well, but I can turn down the heat in lesser used rooms and balance things out. Yes ? No?
Descant is offline   Reply With Quote
Old 02-02-2023, 09:57 PM   #9
John Mercier
Senior Member
 
Join Date: Jun 2021
Posts: 4,009
Thanks: 3
Thanked 680 Times in 562 Posts
Default

I think it has to do with a drop in the BTU output to the point that the unit cannot keep up regardless of how long it runs.
John Mercier is offline   Reply With Quote
Old 02-03-2023, 09:11 AM   #10
BroadHopper
Senior Member
 
BroadHopper's Avatar
 
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,669
Thanks: 3,285
Thanked 1,132 Times in 814 Posts
Default A liitle math

I know the efficiency of my condensing gas boiler and how much it cost per btu.
I also know the efficiency of my split system and how much it cost per btu.

The efficiency of the mini-split drops as the outside temperature drops. I find the cross-over point. This is where I switch to the more efficient heat.

Also, the gas boiler heats up a cold space rather quickly compared to the split system. So I use gas to increase the temperature and switch to the split.

An engineer told me that a split is inefficient when trying to raise the temperature of a cold home. It is efficient in maintaining a set temperature.

So do some research and use your judgment.
__________________
Someday may never be an actual day.
BroadHopper is offline   Reply With Quote
Old 02-03-2023, 09:45 AM   #11
TheProfessor
Senior Member
 
Join Date: Nov 2010
Posts: 1,164
Thanks: 17
Thanked 357 Times in 214 Posts
Default

I view so many new homes such as this.

With fancy dormers. With window bottoms so close to the roof.

Where do these architects think that the snow and melting snow is going to go?
Under dormer windows.
TheProfessor is offline   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -4. The time now is 06:04 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2026, vBulletin Solutions Inc.

This page was generated in 0.16759 seconds