Quote:
As it is, when my power cuts out, it says I have 20 minutes of power. This is adequate to fire up my generator and run a cord to my UPS which also functions nicely as a power distribution node. IMO. The O/P can do much better with a few deep-cycle dry/gel cells and a transformer to prepare for any long term outage if all he wants is heat. Anything more serious and we'd be talking about a generator or solar cell set-up. |
|
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Do you mean Inverter and not "transformer"?
__________________
It's never crowded along the extra mile. |
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,314
Thanks: 67
Thanked 172 Times in 128 Posts
|
|
|
|
|
|
|
#4 | |||
|
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,948
Thanks: 545
Thanked 570 Times in 335 Posts
|
Quote:
In household setups, a 15A circuit is generally the smallest you see, and furnaces are usually on a dedicated circuit. So all this tells us is that your furnace uses anywhere between 1 and 15Amps (well, more like 1 and 12Amps). UPS's have two primary ratings: 1) The max load they can handle (The VA rating) 2) The runtime for a given load (which is usually less than max). Inverter circuitry makes up the VA rating, and the number/size of batteries make up the runtime. You could have 2 different 500Va UPS's, where one could run a given load for 10 minutes, and another with more batteries could run the same load for an hour. Quote:
Quote:
Fundamentally, yes, if he wants the optimal setup from a cost perspective, buy the cheapest inverter that will handle the startup surge current of the furnace, at put as much budget as possible to batteries for max runtime. Then wire it all up properly, being sure to make sure you have adequate wire gauge and connections, and all that.
__________________
[insert witty phrase here] |
|||
|
|
|
|
|
#5 |
|
Senior Member
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
|
I would also be very careful with using a UPS to power your furnace. With a typical UPS, unless you get a Smart UPS (which are very expensive), you risk damaging the electronics in newer furnaces. The controller board needs very clean AC power, of which a typical UPS will not provide.
The same is true for some portable generators. I had a coworker fry the controller board on his new Lennox furnace a couple years back because the Total Harmonic Distortion (i.e. distortion of the input voltage) was not sufficient. |
|
|
|
| Sponsored Links |
|
|
|
|
#6 |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,954
Thanks: 484
Thanked 704 Times in 394 Posts
|
Hmmmm, I'm not sure most of your off the shelf ups systems would be reliable for running a furnace, especially a forced hot air furnace. The motor loads are high and the starting currents are huge, most ups systems will not work reliably unless it is designed specifically for the purpose. A generator would be best for this purpose.
|
|
|
|
|
|
#7 |
|
Senior Member
Join Date: May 2006
Location: Texas, Lake Ray Hubbard and NH, Long Island Winnipesaukee
Posts: 2,971
Thanks: 1,064
Thanked 912 Times in 539 Posts
|
The problem with portable generators is not THD.... the problem with many generators is that they don't regulate the voltage well enough, and spike at 130 or 140 volts which most modern electronic don't handle, and if not fused correctly the electronics get fried when this happens.....
__________________
Life is about how much time you can spend relaxing... I do it on an island that isn't really an island..... |
|
|
|
| The Following User Says Thank You to LIforrelaxin For This Useful Post: | ||
Rusty (10-13-2015) | ||
|
|
#8 |
|
Senior Member
Join Date: Jul 2005
Location: Berlin, Ma / Gilford
Posts: 1,936
Thanks: 452
Thanked 603 Times in 340 Posts
|
All good advice above, but another step we take is to shut off (circuit breaker) the Hot water tank ..... no need in keeping that going
.
__________________
A bad day on the Big Lake (although I've never had one) - Still beats a day at the office!! |
|
|
|
|
|
#9 | |
|
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
__________________
It's never crowded along the extra mile. |
|
|
|
|
|
|
#10 | |
|
Senior Member
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
|
Quote:
http://www.aptsources.com/resources/...Distortion.pdf |
|
|
|
|
| The Following User Says Thank You to HellRaZoR004 For This Useful Post: | ||
Rusty (10-13-2015) | ||
|
|
#11 |
|
Senior Member
Join Date: Jun 2015
Posts: 691
Thanks: 328
Thanked 267 Times in 160 Posts
|
I would not worry so much about back up power and concentrate on getting the water out of the lines. My dad and I used to put a number of camps to bed every year and we just put anti freeze in the toilets and sink traps then made sure the water pipes were drained and left open. Where you run into trouble is if there is a low spot in the pipe that can't be drained. In that case if you have access put in a drain or blow the pipes out with compressed air; not too much pressure. The pipe won't burst from freezing unless they are full of water with no room for the ice to expand.
If the power does go out and a generator kicks on or a battery how long will that last? Unless you have a serious generator it will run out of gas in 3-4 hours. My next thought is to have someone available to check in on the place once in a while and for sure if the power fails. PS don't forget to drain the hose and internals of the washing machine and ice maker. |
|
|
|
|
|
#12 |
|
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,314
Thanks: 67
Thanked 172 Times in 128 Posts
|
|
|
|
|
![]() |