I am a new homeowner on the lake, and am looking for a "part-way" winterization option -- if a safe one exists.
Over the fall and winter we plan to travel up every ~1-2 weeks for weekend visits (our primary home is 2 hours away). I have read several very helpful past threads about winterization -- however most strategies deal with full winterization (fully draining pipes, all appliances, etc). If we performed this every week only to return a week later it would end up being quite the time investment. I was imagining a half-way approach that might include: - keeping home at ~50-55 degrees while gone - opening cabinets with pipes below - pouring antifreeze into drains and toilets - turning off main water feed from well (esp to prevent damage if there is a freeze) I am worried, however, about a power outage (forced air won't work with power out). I also am not sure if there is anything else I should do to protect the well. Any suggestions are much appreciated! If there is no real "half measure" would also appreciate tips on how to make ~weekly process as quick as possible. |
![]() |
![]() |
![]() |
#2 |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,944
Thanks: 544
Thanked 570 Times in 335 Posts
|
![]()
Our place is a true "year round" condo, and is built and insulated for year round use. Some of the below suggestions may vary based on the insulation rating of your place.
We come up frequently throughout the winter, but if I'm working on a project at home it can be 3-4 weeks between visits, so we do a "half winterization" any time we leave after Halloween. Roughly: Set heat back to 50F Turn of main water valve Open faucets to let majority of water drain out. We leave cabinets closed, but that is mostly because the majority of our plumbing is on interior walls and the cabinets don't get particularly frigid. Even if you lose power it will take a while before it gets to freezing temps inside. The way I look at it is that we're close enough (~90 minutes away) that if we get an extended power outage during particularly low temps I might have to drive up mid week or something to ensure everything is OK. So far in the 9 years we've had our place that hasn't been a problem. I have a thermostat that I can check remotely to monitor temps and kick on the heat if necessary. That also mostly lets me track power outages (sometimes power is on but metrocast is out, so I can't be 100% certain that power is on, but if PSNH isn't reporting any outages I'm probably OK). One thing to keep in mind is that sporadic usage can lead to more potential for ice dams if you're not careful. Kicking the heat up, you'll get heat loss through the ceilings and that will melt the snow directly on top of the roof, causing sudden run-off, which will freeze when it hits the edge of the roof. Keeping rooms at a more steady temp (hi or low) reduces this. So I'd also invest in a roof rake and keep the roof clear when you're up there.
__________________
[insert witty phrase here] |
![]() |
![]() |
![]() |
#3 |
Junior Member
Join Date: Oct 2015
Posts: 7
Thanks: 0
Thanked 0 Times in 0 Posts
|
![]()
Very helpful! Thank you
|
![]() |
![]() |
![]() |
#4 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,923
Thanks: 476
Thanked 691 Times in 387 Posts
|
![]()
Need to know a little more about the house, does it have a cellar, are we talking central heat? Insulated?
|
![]() |
![]() |
![]() |
#5 |
Junior Member
Join Date: Oct 2015
Posts: 7
Thanks: 0
Thanked 0 Times in 0 Posts
|
![]()
Thanks.
Central heat -- forced air in attic. There is not a cellar, but crawl space under home is insulated on all sides, with a vent coming down from attic to maintain some heat. Pipes and well located in that crawl space. Previous occupants lived here year round, so had home relatively well insulated. |
![]() |
![]() |
Sponsored Links |
|
![]() |
#6 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,923
Thanks: 476
Thanked 691 Times in 387 Posts
|
![]()
I think you just have to be concerned about freezing pipes with the lowered heat in the crawl space. I'd make sure there are no gross outside air leaks in the crawl space. I would also do the things brk int suggested, especially the freeze alarm, maybe two, with one located in the crawl space. It sounds like the house is pretty well set up, but you won't know until it gets cold.
|
![]() |
![]() |
![]() |
#7 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]()
You can get a battery backup for the furnace. Depending on how many 'cells' it has, they can keep you going quite a while (days).
The most expensive part of the set-up will probably be an automatic switch. You'd probably use the same part as automatic generators use to trip the transfer switch. Good luck! |
![]() |
![]() |
![]() |
#8 |
Senior Member
Join Date: Feb 2007
Location: Loudon, Tennessee, foothills of the Great Smoky Mountains
Posts: 283
Thanks: 340
Thanked 41 Times in 33 Posts
|
![]()
If you are worried about a power outage or the temperature in your home dropping I would suggest looking into a home protection system like one offered by SimpliSafe. You can remotely monitor your house from your smart phone or computer. It will alert you on power outages, home intrusions, flooding and a drop in the home temperature. It will work without power and no phone lines are need because it works off an independent cellular connection. Cost is about $25.00 per month plus initial purchase cost of between $300 to $600. No service contract and you can install it yourself. Company is out of Boston. (Simplisafe.com)
__________________
Moose Tracks |
![]() |
![]() |
![]() |
#9 | |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,944
Thanks: 544
Thanked 570 Times in 335 Posts
|
![]() Quote:
__________________
[insert witty phrase here] |
|
![]() |
![]() |
![]() |
#10 | |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]() Quote:
As it is, when my power cuts out, it says I have 20 minutes of power. This is adequate to fire up my generator and run a cord to my UPS which also functions nicely as a power distribution node. IMO. The O/P can do much better with a few deep-cycle dry/gel cells and a transformer to prepare for any long term outage if all he wants is heat. Anything more serious and we'd be talking about a generator or solar cell set-up. |
|
![]() |
![]() |
![]() |
#11 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
![]()
Do you mean Inverter and not "transformer"?
__________________
It's never crowded along the extra mile. |
![]() |
![]() |
![]() |
#12 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]() |
![]() |
![]() |
![]() |
#13 | |||
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,944
Thanks: 544
Thanked 570 Times in 335 Posts
|
![]() Quote:
In household setups, a 15A circuit is generally the smallest you see, and furnaces are usually on a dedicated circuit. So all this tells us is that your furnace uses anywhere between 1 and 15Amps (well, more like 1 and 12Amps). UPS's have two primary ratings: 1) The max load they can handle (The VA rating) 2) The runtime for a given load (which is usually less than max). Inverter circuitry makes up the VA rating, and the number/size of batteries make up the runtime. You could have 2 different 500Va UPS's, where one could run a given load for 10 minutes, and another with more batteries could run the same load for an hour. Quote:
Quote:
Fundamentally, yes, if he wants the optimal setup from a cost perspective, buy the cheapest inverter that will handle the startup surge current of the furnace, at put as much budget as possible to batteries for max runtime. Then wire it all up properly, being sure to make sure you have adequate wire gauge and connections, and all that.
__________________
[insert witty phrase here] |
|||
![]() |
![]() |
![]() |
#14 |
Senior Member
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
|
![]()
I would also be very careful with using a UPS to power your furnace. With a typical UPS, unless you get a Smart UPS (which are very expensive), you risk damaging the electronics in newer furnaces. The controller board needs very clean AC power, of which a typical UPS will not provide.
The same is true for some portable generators. I had a coworker fry the controller board on his new Lennox furnace a couple years back because the Total Harmonic Distortion (i.e. distortion of the input voltage) was not sufficient. |
![]() |
![]() |
![]() |
#15 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,923
Thanks: 476
Thanked 691 Times in 387 Posts
|
![]()
Hmmmm, I'm not sure most of your off the shelf ups systems would be reliable for running a furnace, especially a forced hot air furnace. The motor loads are high and the starting currents are huge, most ups systems will not work reliably unless it is designed specifically for the purpose. A generator would be best for this purpose.
|
![]() |
![]() |
![]() |
#16 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]() |
![]() |
![]() |
![]() |
#17 |
Senior Member
Join Date: May 2006
Location: Texas, Lake Ray Hubbard and NH, Long Island Winnipesaukee
Posts: 2,862
Thanks: 1,035
Thanked 892 Times in 524 Posts
|
![]()
The problem with portable generators is not THD.... the problem with many generators is that they don't regulate the voltage well enough, and spike at 130 or 140 volts which most modern electronic don't handle, and if not fused correctly the electronics get fried when this happens.....
__________________
Life is about how much time you can spend relaxing... I do it on an island that isn't really an island..... |
![]() |
![]() |
The Following User Says Thank You to LIforrelaxin For This Useful Post: | ||
Rusty (10-13-2015) |
![]() |
#18 |
Senior Member
Join Date: Jul 2005
Location: Berlin, Ma / Gilford
Posts: 1,934
Thanks: 450
Thanked 605 Times in 341 Posts
|
![]()
All good advice above, but another step we take is to shut off (circuit breaker) the Hot water tank ..... no need in keeping that going
.
__________________
A bad day on the Big Lake (although I've never had one) - Still beats a day at the office!! |
![]() |
![]() |
![]() |
#19 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
![]() Quote:
__________________
It's never crowded along the extra mile. |
|
![]() |
![]() |
![]() |
#20 | |
Senior Member
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
|
![]() Quote:
http://www.aptsources.com/resources/...Distortion.pdf |
|
![]() |
![]() |
The Following User Says Thank You to HellRaZoR004 For This Useful Post: | ||
Rusty (10-13-2015) |
![]() |
#21 |
Senior Member
Join Date: Jun 2015
Posts: 662
Thanks: 320
Thanked 250 Times in 149 Posts
|
![]()
I would not worry so much about back up power and concentrate on getting the water out of the lines. My dad and I used to put a number of camps to bed every year and we just put anti freeze in the toilets and sink traps then made sure the water pipes were drained and left open. Where you run into trouble is if there is a low spot in the pipe that can't be drained. In that case if you have access put in a drain or blow the pipes out with compressed air; not too much pressure. The pipe won't burst from freezing unless they are full of water with no room for the ice to expand.
If the power does go out and a generator kicks on or a battery how long will that last? Unless you have a serious generator it will run out of gas in 3-4 hours. My next thought is to have someone available to check in on the place once in a while and for sure if the power fails. PS don't forget to drain the hose and internals of the washing machine and ice maker. |
![]() |
![]() |
![]() |