I'm looking for a reliable HVAC contractor to perform a replacement of a old Oil boiler with a new 3 pass boiler. I'm looking at the Weil Mclain Ultra Oil boiler or the Buderus G115w boiler. I was interested in the Burnham 3 pass units as well but pre sales info request from Burnham was met with rude responses from the factory so I'm leaving them out of the mix.
I'm also looking at a "direct vent" option using a Riello burner as a way to get rid of the power vent I have now. No chimney is available. I'd welcome replies from anyone who has installed a direct vent oil system in the past few years. I'm in Gilford. Any response it welcome. Thanks Charlie T |
![]() |
![]() |
![]() |
#2 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() Quote:
I went with an HB Smith boiler because I needed a side clean out due to space constraints, it's in a crawl space. I wish I could help you out on a contractor. I get my oil from Stafford Oil and I know they install boilers. |
|
![]() |
![]() |
![]() |
#3 |
Senior Member
|
![]()
Is always best to go first class for heat and hot water ....... go RIELLO (Italy) and go RINNAI (Japan) and you won't go a-wrong!
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
The Following User Says Thank You to fatlazyless For This Useful Post: | ||
Charlie T (09-05-2018) |
![]() |
#4 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() |
![]() |
![]() |
The Following User Says Thank You to Biggd For This Useful Post: | ||
BroadHopper (09-06-2018) |
![]() |
#5 |
Senior Member
|
![]()
Just checked at walmart.com and yes, to my surprise, it has Rinnai natural gas and propane items.
For $954.29 walmart.com will ship you, free freight, to a Walmart store, a 24,000-btu naural gas or propane Rinnai wall furnace. Believe this same item costs about $1500 at Amerigas in Laconia. Back in 1998, I got one for the then discount price of about $800, installed it myself, and it has worked totally perfect ever since, with no maintenance what-so-ever.... the greatest, most reliable, warm & comfy hot air heater ever made ..... now comes in beige or white. With the recent spat of global warming, will heat still be needed in the winter?
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
Sponsored Links |
|
![]() |
#6 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() Quote:
But that's beside the point, the OP said he has oil and they don't make those wall units for oil. |
|
![]() |
![]() |
The Following User Says Thank You to Biggd For This Useful Post: | ||
Charlie T (09-05-2018) |
![]() |
#7 |
Senior Member
|
![]()
....omg ...... the walmart.com has Riello which is oil, super duper quality, efficiency, made in Italy!
What is the world coming to, when walmart.com has these types of installer items ....... lord have mercy..... on the poor slob who installs it hisself?
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
![]() |
#8 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,925
Thanks: 476
Thanked 691 Times in 387 Posts
|
![]()
Charlie, I had several bad experiences with the Burnham castings cracking (happened twice on my boiler) so I pulled it and installed a Buderus. Too lazy to go downstairs and see which model, but I believe it is the 215. I opted for the Logamatic 2107 control which was an additional $1,200 I believe but would not do that again. I have forced hot water baseboard, the 2107 is designed for European systems which have dial type thermostats on the radiators which control each room, not the systems typically found here.
My baseboards need hot water to convect properly, the basis of the 2107 is that it provides cooler water when the temperature is warmer outside which works well for European style radiators but not too well for baseboard. My issue is on mainly spring/late winter days where it is cold at night but warms up quickly in the morning. The house is cold, but the control sees it's warmer outside so it send cooler water to the baseboard which doesn't really heat the house that well. It's a small issue, but I think a basic cold start control would work better for baseboard, or a control that is designed specifically for baseboard if you want to vary the temps. That said, we used to burn somewhere in the area of 1,000+ gallons of oil a winter season, the new boiler burned about 600 gallons last year so it did save us money. If you have radiant floor heat then the 2107 control is probably ideal for that. I use Foley oil and I know they do installs, but not sure what boilers they use. I've been thinking about changing out my Winnipesaukee boiler, but it is pretty efficient and still in good shape. Good luck. |
![]() |
![]() |
The Following User Says Thank You to ITD For This Useful Post: | ||
Charlie T (09-05-2018) |
![]() |
#9 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
Yes there are cheaper boilers out there, but if you want the most efficient this company is it. Buderus is only the block not a system, it's not efficient and needs a high static burner like a Riello and is very noisy. As someone has mentioned, stay away from wall hung units, they're being installed on baseboard systems that will lead to their premature failure. Wall hung boilers are designed for low temp applications so if you're doing a radiant of fan coil system you'll be fine. Good luck |
|
![]() |
![]() |
![]() |
#10 | |
Senior Member
Join Date: Apr 2016
Location: In the hills
Posts: 2,420
Thanks: 1,677
Thanked 786 Times in 466 Posts
|
![]() Quote:
We have the Buderus forced hot water furnace/boiler and the water heater. Fueled by propane they seem efficient enough. Fill me in please! |
|
![]() |
![]() |
![]() |
#11 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#12 | |
Senior Member
Join Date: Apr 2016
Location: In the hills
Posts: 2,420
Thanks: 1,677
Thanked 786 Times in 466 Posts
|
![]() Quote:
In other words a forced hot water by propane system. I had a heating guy come by to clean it and he said it was so clean inside he really didn’t have much to clean but he still charged me $200 |
|
![]() |
![]() |
The Following User Says Thank You to Hillcountry For This Useful Post: | ||
Charlie T (09-05-2018) |
![]() |
#13 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#14 |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]()
I was considering a Burnham 3 pass boiler until I tried to get some info on the direct vent feature directly from Burnham . I could find nothing on the website so I filled out a detailed online form with my name, address and contact info asking for what I needed. I got a snippy email back from the "customer service dept" telling me they don't talk to homeowners and certainly would not provide me with any info on their products. I was then informed that if I wanted that info I should go thru their website to find out who the " local distributor" was in my area and that they might be able to help me. If I wanted the run around I would not have gone directly to the source. If this is how they treat potential customers I can just imagine how little regard they would have for me once my money was in their hands. Burnham fell right off the list of boiler choices for me
|
![]() |
![]() |
![]() |
#15 |
Senior Member
Join Date: Apr 2016
Location: In the hills
Posts: 2,420
Thanks: 1,677
Thanked 786 Times in 466 Posts
|
![]()
This is what we have: lol they look wall mounted but they are indeed on the floor!
|
![]() |
![]() |
![]() |
#16 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
You have a Buderus g124 atmospheric propane fired boiler with indirect. The AFUE rating are determined by the manufacturer of the equipment and not a factual rating of efficiency. Blue sure looks purty though... Don't get me wrong it will heat your home and hot water. I believe the poster was looking to replace an oil fired unit which is much different than gas.
What you'll find is that most installers will install what they feel comfortable installing and can care less about efficiency or whether the system is truly compatible with what you have now. https://energykinetics.com/wp-conten...lsResearch.pdf |
![]() |
![]() |
The Following User Says Thank You to swnoel For This Useful Post: | ||
Hillcountry (09-06-2018) |
![]() |
#17 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]()
I've had a dozen homes over my 65 years, mostly with oil fired boilers, and they have all had either Weil Mclain or HB smith boilers that have lasted 25 years or more with no major issues.
Sometimes going with the new technology has it's pit falls. A lot more head aches for a little more efficiency? |
![]() |
![]() |
![]() |
#18 | |
Moderator
|
![]() Quote:
When I posted a picture on FB of the ancient boiler being removed a friend posted a picture of his brand new wall hung on demand system and bragged how it was so efficient and cutting edge. The next time I saw him they said that shortly after that post they started having problems that took the heating contractor a few weeks to resolve. We're so glad we went with a traditional time proven Weil McLain boiler. It has cut our gas bill by at least 2/3's and we haven't had a single problem with it. Since the spring every gas bill has been under $30 and that's only because the boiler also heats the hot water. I feel we made the right choice. Here's a picture of the old beast being hauled away. The removal crew said "By next month this will be a Kia". |
|
![]() |
![]() |
The Following 3 Users Say Thank You to webmaster For This Useful Post: | ||
![]() |
#19 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]()
The house I live in now is my family home which I remodeled in 1995 after my mother passed away. I had a boiler that was about 5ft square removed and installed a Weil Mclain that was about 1/4th the size. Still to this day no major issues, just a few electronic controls replaced over the years. My burner guy says it's fine and no reason to change it but I did just replace my indirect water heater after 23 years.
The only thing I regret is not switching to gas back in 1995 as there is a gas line in the street. I'm hoping I'm not there long enough for another boiler change. I built the house behind me back in 1984 and installed an HB Smith boiler and the guy just replaced it a few years ago. Both, my brother inlaw and my best friend, had the gas fired wall hung units installed within the past 5 years and have had nothing but problems with them every winter. One had to be completely changed under warrantee and the both have gone through a few circuit board changes. Last edited by Biggd; 09-06-2018 at 10:28 AM. |
![]() |
![]() |
![]() |
#20 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
![]()
FWIW my Burnham boiler with a Beckett burner has been going strong for 28 years. Had a Boderus installed in dads house and really like it. The techs rave about them also.
__________________
SIKSUKR |
![]() |
![]() |
![]() |
#21 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]()
Burnham's been around a long time but my heating guy says that's the #1 boiler that he replaces because of leaks. I guess you got your moneys worth.
|
![]() |
![]() |
![]() |
#22 | |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]() Quote:
I"m hoping to find a reputable local installer who can help me select that unit. |
|
![]() |
![]() |
![]() |
#23 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
Low mass and post purge... what's value engineered? |
|
![]() |
![]() |
![]() |
#24 |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]()
The overwhelming issues that appear to be showing up with modern hi efficiency boilers is cracking and leaking. The units they replaces lasted 30, 50, 70 years and were probably functional when they were replaced. The issues with the newer ones appear to be lower quality materials and fllaws in design and QC that allow them to get out the shipping dock. That to me is the result of Value engineering.
This is a worldwide problem in virtually every industry where bean counters calculate the overall cost of warranty costs vs building a better product. Part of the calculation is income from replacement parts for non warranty repairs, this is the reason our homes are filled with junk that doesn't last as long as it should. A prime example is automobiles, as the manufacturers quality increased the warranties were extended to 100K miles, in the past few years the trend has been to reduce the warranty. Try to find a new car now with a 100K power train warranty today....... What was the norm 5 year ago is now extinct. Build the product only as good as you have to and expect / hope for a return customer when it breaks once out of warranty |
![]() |
![]() |
![]() |
#25 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
I agree, most US boiler manufacturer have reduced the thickness of their castings and many leak prematurely or crack. This is why steel is a good option. Quality Control??? LOL Stay away from wall hung units that claim 95% efficiencies on Baseboard systems...you'll be lucky to get 10 years out of them! |
|
![]() |
![]() |
![]() |
#26 | |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]() Quote:
If I can only compile a list of local contractors that people have had good luck with. Does anybody have any names they can share / recommend? Thanks |
|
![]() |
![]() |
![]() |
#27 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#28 | |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,925
Thanks: 476
Thanked 691 Times in 387 Posts
|
![]() Quote:
For the OP, I had a power venter, I hated that thing, it was loud and not very reliable. I also disliked having the discharge low to the ground as the fumes always found a way into an open window in the summer. So I ditched the power venter and put a stainless chimney up the side of the house. The chimney was a thousand or two more than another power vent would have been, but has no reliability issues and I don't smell burning fuel oil when my boiler kicks in for my hot water storage tank. YMMV. |
|
![]() |
![]() |
The Following User Says Thank You to ITD For This Useful Post: | ||
swnoel (09-09-2018) |
![]() |
#29 |
Senior Member
Join Date: Dec 2006
Posts: 683
Thanks: 127
Thanked 85 Times in 49 Posts
|
![]()
Put in a Weil McLain Gold oil burner 10 years ago. Zero issues. Going too high end seems to be problematic from all the research I have done.
It's still running 84% efficiency, down from 87% when I purchased it. Just a solid, decently priced machine. |
![]() |
![]() |
![]() |
#30 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
LOL... that boiler isn't 84% efficient. That efficiency is the burn of the burner not the efficiency of the boiler which can be high until is reaches steady state.
|
![]() |
![]() |
![]() |
#31 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
![]()
It could be the annual fuel utilization efficiency (AFUE) that he is talking about.
__________________
It's never crowded along the extra mile. |
![]() |
![]() |
![]() |
#32 |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]()
All good info from everyone..... Thank you !!
Does anyone have recommendations for installer companies that you can highly recommend?. Everything I've read and everything I know from my profession tells me that the install/ service company is every bit as important as the equipment. Thanks Charlie T |
![]() |
![]() |
![]() |
#33 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
No it can't... only the manufacturer can manipulate that! He's talking about the efficiency the tech told him his boiler was after they did the combustion test. I've done thousands of them.
|
![]() |
![]() |
![]() |
#34 |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]()
The reading the tech is taking using a probe in the stack is simply a combustion efficiency number that is based upon gas readings in the stack after it has left the boiler. This only is a measurement of how well the burner is turning fuel into heat energy, it has nothing to do with how efficiently the boiler is collecting that heat energy and transferring it to the water in your boiler/ heating system. The trick to saving money is to transfer as much of the heat energy into energy that is actually used to heat your premises. This is where the science, magic, Voodoo and unfortunately creative marketing come into play.
|
![]() |
![]() |
![]() |
#35 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() Quote:
I've busted up a few Weil Maclain boilers that were 25 plus years old, to get them out of a basement or crawlspace, and the were still pretty solid and leak free. Finding an installer that won't cost you and arm and a leg will be the difficult part. |
|
![]() |
![]() |
![]() |
#36 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#37 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() Quote:
As far as cars go, I'm an auto mechanic by trade and most of the cars today are far superior to any cars made 30 years ago. As a matter of fact some of the worst cars ever built where made in the 80's. I will agree that appliances are crap today though. I'm 65 so as long as it outlasts me I'm fine. ![]() Last edited by Biggd; 09-10-2018 at 12:36 PM. |
|
![]() |
![]() |
![]() |
#38 | |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
![]() Quote:
__________________
SIKSUKR |
|
![]() |
![]() |
![]() |
#39 |
Senior Member
Join Date: Dec 2006
Posts: 683
Thanks: 127
Thanked 85 Times in 49 Posts
|
![]()
It is the AFUE. Considering that you have no idea that new cars are far superior these days to older ones I'll take any of your future info with a grain of salt.
|
![]() |
![]() |
![]() |
#40 | |
Senior Member
Join Date: Apr 2008
Location: Moultonborough
Posts: 750
Thanks: 4
Thanked 259 Times in 171 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#41 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
LOL... cars of yesteryear had more metal in their front fenders than most cars today have in their entirety! I use to be able to fix my own ...today you need a multi thousand dollar computer do do just about anything! I don't care what you do ... but I can assure you that I've forgotten more about heating systems and their operations than probably everyone that has posted here! I always get a laugh when the weekend pros just their advice...
|
![]() |
![]() |
![]() |
#42 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() |
![]() |
![]() |
![]() |
#43 |
Senior Member
Join Date: Apr 2004
Posts: 309
Thanks: 256
Thanked 183 Times in 88 Posts
|
![]()
Does anyone have recommendations of quality install companies in the lakes region??? That is truly what I"m looking for.
Thank you Charlie T |
![]() |
![]() |
![]() |
#44 | |
Senior Member
Join Date: Dec 2006
Posts: 683
Thanks: 127
Thanked 85 Times in 49 Posts
|
![]() Quote:
If you tell me that new toasters at Walmart don't match up with older ones....than we can agree. Cars & planes. No sell. |
|
![]() |
![]() |
![]() |
#45 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() Quote:
![]() |
|
![]() |
![]() |
![]() |
#46 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,110
Thanks: 2,219
Thanked 1,189 Times in 756 Posts
|
![]() |
![]() |
![]() |
![]() |