Quote:
Originally Posted by bigdog View Post
My Propane furnace seems to be constantly running and not sure why ?
Stats: Trans 90 XL (90k BTU output)

Gas service tech checked furnace and nothing appears to be wrong, all 3 gas jets firing OK.

The thing is the zone thermostat (Honeywell( indicates the tempperature is set at 67 degrees, however, the room temperature reading indicates 65 degrees.
Consequently the furnace never shuts down because it is constantly calling for heat to reach the thermostat setting.

New batteries were installed in 'all' house thermostats.

Do you think I have a bad thermostat ?

Thanks,
BD

This is common when a furnace is under fired. It might say 90K btu's on the tag, but if the gas line is too small it will only allow whatever the line size does. Have you ever had problems in cold weather before? Could be the thermostat, is it a programmable? Is this a zoned system... check the dampre and make sure it's opened all the way.
swnoel is offline   Reply With Quote
 

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 06:50 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.

This page was generated in 0.17472 seconds